the size of the battery bank is much more to do with what you need to take out of the system, rather than what you use to put it in! :wink:
If you're drawing 70amp/hrs in a day, you'll need ten times that (700amp/hrs), minimum battery bank size, as you shouldn't aim to take more than 10% out in a day! This isn't me trying to flog you lots of batteries - it is a pragmatic "rule of thumb" to ensure reasonable and economic battery life and performance! :geek: